Andrew M.A. Cater wrote:
> On Mon, Apr 27, 2009 at 11:56:24AM -0700, Lux, James P wrote:
>> Urban legend.
>> Do the math and calculate how many turns it takes, and don't forget that 
>> those wires have some non-zero resistance. So, unless you happen to have a 
>> large vat of liquid helium and lots of superconductors, the "stealing power 
>> by capacitive/inductive coupling" is probably bogus.
>>
>> Don't forget that "real" power lines tend to be fairly well balanced, so the 
>> net field at any reasonable distance is quite low.
>>
>> Detect the field, certainly.
>> Get some trivial amount of mechanical work out of the system (spin a low 
>> mass dial or something), probably.
>> Power your house/barn/dairy shed, not a chance.
>>
>> Let's use real numbers: 1000A, unbalanced, 20m away  (extremely unlikely 
>> that 1000A unbalanced, but we'll go ahead anyway)
>>
>> Ampere's law
>> B = mu0 * I/(2*pi*r)
>>   = 4*pi*1E-7 * 1000 /(2*pi*20)
>>   = 2E-7*1000/20 = 2E-4/2E1 = 1E-5  Tesla  (note Earth field is 0.5E-4 T)
>>
>>
>>
>>
>> Faraday's law of induction
>> V = -dPhi/dt = -N*Area*dB/dt
>> dB/dt = omega*cos(omega*t)*Bpk (for sinusoid)
>>      = 2*pi*f*Bpk = 377*Bpk (for 60Hz)
>>
>> Let's assume that Bpk = 1.414Brms (because the above Ampere's law 
>> calculation assumed 1000A rms)
>>  dB/dt = 377*1.414*1E-5 T/s = 0.005 T/s
>>
>> OK. We're going to put that big coil along our roof.  Let's say 2m by 10m, 
>> so the area is 20 square meters.  The induced voltage per turn is 20*.005 = 
>> 0.1 Volt.  That's pretty low, so let's use 100 turns, so the voltage is now 
>> 10 Volts.  But, the length of the wire in that coil is 22 meters/turn, so 
>> we've got about 2200 meters of wire.   Assume it's AWG20 (fairly small, but 
>> not too small that it will easily break), which has a resistance of about 10 
>> ohms/1000ft (sorry for the US units) or, 72 ohms total for our 100 turn 
>> coil. That works out to about 130mA, so we actually are going to dissipate 
>> about 1.4Watts in the coil. The optimum load impedance is also 72 ohms, so 
>> if we do that, we'll have half the current, and we'll capture a whopping 
>> 350mW in our load.
>>
>> Let's see.. At $0.34/kWh (the peak rate I pay at home), assuming I do this 
>> big coil thing for a year (8000 hours), I will have scammed the power 
>> company for 8000*.35 = 2.8kWh or about a dollar's worth of electricity.
>>
>> Leaving aside the substantial labor, I also had to go out and buy about 10kg 
>> of copper wire, which is about $5-10/kg, depending on the copper market.  So 
>> I spent $50-100 on wire.  The payback period is 50-100 years.
>>
> 
> Beautifully done. The version I'd heard - which is fractionally more 
> plausible - is that the person concerned lived next to one of the Royal 
> Navy's submarine communication transmitters operating at lower than 
> 16KHz. These things run megawatts at piddling efficiency to get watts 
> output because the antenna matching is so poor. Said anonymous bloke - 
> they're always anonymous - allegedly tuned his heating system to 
> resonance therefore acting as a lossy dummy load and, incidentally, 
> heating his water. Found only because there was an arc of the N. 
> Atlantic where there was no signal AT ALL and the subsequent 
> investigation turned up what he'd done. He wasn't receiving the signal 
> content per se - so no unauthorised interception - and he couldn't be 
> prosecuted readily so they agreed to forget about it.
> 

My favorite characteristic of these urban legends is that anyone smart
enough to pull off a trick like this is probably already making enough
money that they don't need to steal electricity.


-- 
Prentice
_______________________________________________
Beowulf mailing list, Beowulf@beowulf.org sponsored by Penguin Computing
To change your subscription (digest mode or unsubscribe) visit 
http://www.beowulf.org/mailman/listinfo/beowulf