We are pretty much sticking with Pulz power supplies unless engineers call
for Phoenix Contact....Yes pricier , but they hold up well....In lieu of
that, add protection .....

On Mar 26, 2017 6:05 PM, "Jaime Solorza" <[email protected]> wrote:

> If you are using mean well supplies test them carefully to see how they
> behave in a inrush or short circuit event.   The SD series, on over
> current, lock out until the input power is removed for ~10 seconds.    This
> can be a real problem if the inrush current of your load is sufficient to
> trip them into lockout.     Sometimes hard to see when you are starting up
> a site or a site has equipment added to it after it’s been in operation for
> a while.  Power goes out, comes back on and the power supply locks out due
> to inrush current.   Very annoying.
>
> The RSD series does not have this issue.
>
> In any case - test your designs carefully.
>
> Mark
>
> On Mar 26, 2017, at 9:07 PM, Bill Prince <[email protected]> wrote:
>
> Check the specs on the Meanwell. Most good power supplies do have current
> limiting built in. Most of them you can short the output and they will
> limit to whatever the current limit is.
>
> bp
> <part15sbs{at}gmail{dot}com>
>
>
> On 3/26/2017 4:57 PM, Adam Moffett wrote:
>
> I just replaced a Meanwell SDR-240-48 today.  I have no reason to think
> there was a surge, but it made me think of the thread about the Netonix
> POE and surge suppressors.  If a DC surge protector clamps, am I shorting
> my DC power supply?  What's likely to happen?
>
> This unit is supposed to have protection for over voltage and overload
> conditions.  It doesn't specifically say anything about short
> circuit....but I assume a short leads (rapidly) to an overload so maybe it
> would be ok?
>
>
>
>
>
>

Reply via email to