If you are using mean well supplies test them carefully to see how they behave 
in a inrush or short circuit event.   The SD series, on over current, lock out 
until the input power is removed for ~10 seconds.    This can be a real problem 
if the inrush current of your load is sufficient to trip them into lockout.     
Sometimes hard to see when you are starting up a site or a site has equipment 
added to it after it’s been in operation for a while.  Power goes out, comes 
back on and the power supply locks out due to inrush current.   Very annoying.

The RSD series does not have this issue.

In any case - test your designs carefully.

Mark 

> On Mar 26, 2017, at 9:07 PM, Bill Prince <[email protected]> wrote:
> 
> Check the specs on the Meanwell. Most good power supplies do have current 
> limiting built in. Most of them you can short the output and they will limit 
> to whatever the current limit is.
> 
> bp
> <part15sbs{at}gmail{dot}com>
> 
> On 3/26/2017 4:57 PM, Adam Moffett wrote:
>> I just replaced a Meanwell SDR-240-48 today.  I have no reason to think 
>> there was a surge, but it made me think of the thread about the Netonix POE 
>> and surge suppressors.  If a DC surge protector clamps, am I shorting my DC 
>> power supply?  What's likely to happen?
>> 
>> This unit is supposed to have protection for over voltage and overload 
>> conditions.  It doesn't specifically say anything about short circuit....but 
>> I assume a short leads (rapidly) to an overload so maybe it would be ok?
>> 
>> 
> 
> 

Reply via email to