Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
Rick: Two questions: 1. If you don’t have PV on this system, what are those glassy, flat things on the roof wired to the DC inputs of your Sunny Boy? 2. Think to yourself: What component(s) on this project could possibly produce high voltage DC? I think the answer to both questions

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
William, There’s no PV on this system. It’s AC coupled to an SMA SB5.0. As a test, we turned off the Grid input, Load output, and turned off the battery breaker. As expected, the high voltage DC eventually bled to 0V. Turning things on in this order: Battery, Grid, then Load resulted in the hi

Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

2024-10-15 Thread Jason Szumlanski via RE-wrenches
I am happy to report that these issues are resolved, and the system is operating normally after replacing the broken MC4 and re-pulling wire for the home run of the faulted string. That second issue emanated from my guys pulling wire through a conduit underground that evidently had some rocks in i

Re: [RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread William Miller via RE-wrenches
Rick: If I had to guess I’d say you have a PV wiring fault. The PV positive may be shorted to ground. This would make the inverter chassis negative in relation to ground. The logic I use is to ask what is the likely source of DC at 195 volts? It is most likely the PV circuits, wouldn’t you

[RE-wrenches] Sol-Ark Gen Input

2024-10-15 Thread rick--- via RE-wrenches
Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V. I know the Gen input can be configured as an output, but reading a high DC voltage to ground is concerning. The generator has never been run. Sys

Re: [RE-wrenches] All-In-Ones / Sol-Ark fail

2024-10-15 Thread Jason Szumlanski via RE-wrenches
I like the idea of an ATS, but the customer would need to choose (in this case) whether they want the house to go dark or to burn through 2000 gallons of propane if left unattended. When you have to barge out a propane truck to refill, the economics change. You would not even need an ATS if the So