I'm running Raspbian GNU/Linux 10 (buster) on a Raspberry Pi 4.
I have nut-client and nut-server version 2.7.4-8 armhf installed from the
Raspbian Buster main apt repository.
I have a Tripp Lite AVR900U series AG-0309 connected via USB to the Pi. The
USB vendor ID is 09ae as expected, but the product ID is 3024. The
compatibility page at
https://networkupstools.org/ddl/Tripp_Lite/AVR900U.html says the product ID
is expected to be 2010.
There's no manufacturing date printed on the UPS or box, but I bought it
from Amazon.com this week.


I have these settings:

/etc/nut/ups.conf
[tripplite]
        driver = usbhid-ups
        port = auto
        desc = "Tripp Lite AVR900U"
        vendorid = 09ae
        productid = 3024

/etc/nut/nut.conf
MODE=standalone


Starting from the beginning, this fails:
systemctl restart nut-driver.service
I see that it tries to run:
/sbin/upsdrvctl start
This also fails. I added debug flags, and discovered that it's running this:
/lib/nut/usbhid-ups -a tripplite
Which also fails. I added debug flags to that, and got useful output, which
I'll show you now.


root@raspberrypi4:~# /lib/nut/usbhid-ups -a tripplite -DDDDDD
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000 debug level is '6'
   0.000830 upsdrv_initups...
...
   0.002583 Checking device (09AE/3024) (001/004)
   0.002638 - VendorID: 09ae
   0.002660 - ProductID: 3024
   0.002679 - Manufacturer: unknown
   0.002700 - Product: unknown
   0.002724 - Serial Number: unknown
   0.002746 - Bus: 001
   0.002770 - Device release number: 0002
   0.002790 Trying to match device
   0.002814 This TrippLite device (09ae:3024) is not (or perhaps not yet)
supported
by usbhid-ups. Please make sure you have an up-to-date version of NUT. If
this does not fix the problem, try running the driver with the
'-x productid=3024' option. Please report your results to the NUT user's
mailing list <[email protected]>.

   0.002854 Device does not match - skipping
...
   0.003689 No appropriate HID device found
   0.003714 No matching HID UPS found


I'm not sure if USB info would be useful for you, but if it is, here it is:

root@raspberrypi4:~# lsusb --verbose
Bus 001 Device 004: ID 09ae:3024 Tripp Lite
Device Descriptor:
  bLength                18
  bDescriptorType         1
  bcdUSB               2.00
  bDeviceClass            0
  bDeviceSubClass         0
  bDeviceProtocol         0
  bMaxPacketSize0        64
  idVendor           0x09ae Tripp Lite
  idProduct          0x3024
  bcdDevice            0.02
  iManufacturer           3 Tripp Lite
  iProduct                1 AVR900U
  iSerial                 5 3050BV4OM882300258
  bNumConfigurations      1
  Configuration Descriptor:
    bLength                 9
    bDescriptorType         2
    wTotalLength       0x0022
    bNumInterfaces          1
    bConfigurationValue     1
    iConfiguration          0
    bmAttributes         0xa0
      (Bus Powered)
      Remote Wakeup
    MaxPower              100mA
    Interface Descriptor:
      bLength                 9
      bDescriptorType         4
      bInterfaceNumber        0
      bAlternateSetting       0
      bNumEndpoints           1
      bInterfaceClass         3 Human Interface Device
      bInterfaceSubClass      0
      bInterfaceProtocol      0
      iInterface              0
        HID Device Descriptor:
          bLength                 9
          bDescriptorType        33
          bcdHID               1.11
          bCountryCode           33 US
          bNumDescriptors         1
          bDescriptorType        34 Report
          wDescriptorLength     885
         Report Descriptors:
           ** UNAVAILABLE **
      Endpoint Descriptor:
        bLength                 7
        bDescriptorType         5
        bEndpointAddress     0x81  EP 1 IN
        bmAttributes            3
          Transfer Type            Interrupt
          Synch Type               None
          Usage Type               Data
        wMaxPacketSize     0x0040  1x 64 bytes
        bInterval             255
can't get device qualifier: Resource temporarily unavailable
can't get debug descriptor: Resource temporarily unavailable
Device Status:     0x0002
  (Bus Powered)
  Remote Wakeup Enabled


To get usbhid-ups to try communicating with the UPS anyways, I added this
udev rule and then unplugged and plugged back in the USB cord:

/lib/udev/rules.d/62-nut-usbups.rules
ATTR{idVendor}=="09ae", ATTR{idProduct}=="3024", MODE="664", GROUP="nut"


It looks like forcing usbhid-ups to communicate works, maybe? I'm not sure
what's expected here:

root@raspberrypi4:~# /lib/nut/usbhid-ups -a tripplite -DD -x productid=3024
-x explore
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000 debug level is '2'
   0.002081 upsdrv_initups...
...
   0.005719 Checking device (09AE/3024) (001/009)
   0.011434 - VendorID: 09ae
   0.011499 - ProductID: 3024
   0.011541 - Manufacturer: Tripp Lite
   0.011587 - Product: AVR900U
   0.011631 - Serial Number: 3050BV4OM882300258
   0.011674 - Bus: 001
   0.011719 - Device release number: 0002
   0.011761 Trying to match device
   0.011890 Device matches
   0.014215 HID descriptor length 885
   0.018081 Report Descriptor size = 885
   0.018945 Using subdriver: EXPLORE HID 0.1
   0.018992 87 HID objects found
   0.020830 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28,
Offset: 0, Size: 8, Value: 1
   0.021572 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID:
0x29, Offset: 0, Size: 8, Value: 5
   0.022377 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID:
0x2b, Offset: 0, Size: 8, Value: 3
   0.022965 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature,
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.023703 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID:
0x31, Offset: 0, Size: 16, Value: 0.001254
   0.024453 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 3
   0.025201 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.025263 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.025320 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.025375 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.025431 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.025490 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.025546 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.025601 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   0.025656 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 1
   0.025710 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.025768 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.025820 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.025875 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.025929 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type:
Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   0.025983 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x32, Offset: 20, Size: 1, Value: 1
   0.026038 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.026092 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.026149 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.027950 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
   0.028693 Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x62, Offset: 0, Size: 8, Value: 2
   0.029319 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID:
0x33, Offset: 0, Size: 8, Value: 2
   0.029957 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 94
   0.030016 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x34, Offset: 0, Size: 8, Value: 94
   0.030583 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature,
ReportID: 0x37, Offset: 0, Size: 8, Value: 100
   0.031318 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID:
0x36, Offset: 0, Size: 8, Value: 100
   0.031943 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x38, Offset: 0, Size: 8, Value: 30
   0.032697 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID:
0x2c, Offset: 0, Size: 8, Value: 1
   0.033446 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 3650
   0.033507 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID:
0x35, Offset: 0, Size: 16, Value: 3650
   0.034195 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 16, Value: 12
   0.034945 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature,
ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000137
   0.035581 Path:
UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
   0.035641 Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged,
Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 0
   0.035697 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type:
Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 1
   0.035752 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging,
Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
   0.035806 Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged,
Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
   0.035861 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement,
Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
   0.038212 Path: UPS.BatterySystem.Battery.RemainingCapacity, Type:
Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 94
   0.038944 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID:
0x10, Offset: 0, Size: 8, Value: 6
   0.039705 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01,
Offset: 0, Size: 8, Value: 120
   0.040453 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02,
Offset: 0, Size: 8, Value: 60
   0.041199 Path: UPS.Flow.ffff0097, Type: Feature, ReportID: 0x55, Offset:
0, Size: 8, Value: 2
   0.041950 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID:
0x03, Offset: 0, Size: 16, Value: 900
   0.042589 Path: UPS.PowerConverter.Input.Voltage, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 0.001254
   0.043213 Path: UPS.PowerConverter.Input.Frequency, Type: Feature,
ReportID: 0x19, Offset: 0, Size: 16, Value: 6020
   0.043713 Path: UPS.PowerConverter.Output.Voltage, Type: Feature,
ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.001264
   0.044211 Path: UPS.PowerConverter.Output.Frequency, Type: Feature,
ReportID: 0x1c, Offset: 0, Size: 16, Value: 6020
   0.044835 Path: UPS.PowerConverter.Output.Current, Type: Feature,
ReportID: 0x46, Offset: 0, Size: 16, Value: 0
   0.045573 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature,
ReportID: 0x47, Offset: 0, Size: 16, Value: 0
   0.046325 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type:
Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 89
   0.047075 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type:
Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 145
   0.047823 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type:
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.047880 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature,
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.047933 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature,
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.047986 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature,
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.048040 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature,
ReportID: 0x22, Offset: 5, Size: 1, Value: 1
   0.048098 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type:
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.048151 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type:
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.048204 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type:
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.050451 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type:
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.051202 Path: UPS.OutletSystem.Outlet.ffff0056, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
   0.051951 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.052704 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type:
Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   0.053450 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature,
ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
   0.054199 Path: UPS.OutletSystem.Outlet.ffff0081, Type: Feature,
ReportID: 0x41, Offset: 0, Size: 8, Value: 0
   0.054953 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature,
ReportID: 0x51, Offset: 0, Size: 8, Value: 0
   0.055699 Path: UPS.OutletSystem.Outlet.ffff0092, Type: Feature,
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.056451 Path: UPS.ffff00fe.ffff0075, Type: Feature, ReportID: 0x0d,
Offset: 0, Size: 8, Value: 6
   0.057199 Path: UPS.ffff00fe.ffff0076, Type: Feature, ReportID: 0x0e,
Offset: 0, Size: 8, Value: 7
   0.057837 Path: UPS.ffff00fe.ffff007c, Type: Feature, ReportID: 0x0f,
Offset: 0, Size: 8, Value: 162
   0.058574 Path: UPS.ffff00fe.ffff009c, Type: Feature, ReportID: 0x43,
Offset: 0, Size: 8, Value: 1
   0.059086 Path: UPS.ffff00fe.ffff00a0, Type: Feature, ReportID: 0x57,
Offset: 0, Size: 8, Value: 0
   0.059698 Path: UPS.ffff00fe.ffff00a1, Type: Feature, ReportID: 0x58,
Offset: 0, Size: 8, Value: 0
   0.060435 libusb_get_report: error sending control message: Operation not
permitted
   0.060491 Can't retrieve Report 59: Operation not permitted
   0.060545 Path: UPS.ffff00fe.ffff00a2, Type: Feature, ReportID: 0x59,
Offset: 0, Size: 8
   0.061202 Path: UPS.ffff00fe.ffff007d, Type: Feature, ReportID: 0x6c,
Offset: 0, Size: 16, Value: 12324
   0.061948 Path: UPS.ffff00fe.ffff0062, Type: Feature, ReportID: 0x5d,
Offset: 0, Size: 8, Value: 1
   0.062686 libusb_get_report: error sending control message: Operation not
permitted
   0.062741 Can't retrieve Report 60: Operation not permitted
   0.062792 Path: UPS.ffff00fe.ffff0060, Type: Feature, ReportID: 0x60,
Offset: 0, Size: 8
   0.063455 Path: UPS.ffff00ff.ffff00d6, Type: Feature, ReportID: 0xc2,
Offset: 0, Size: 32, Value: 1.76439e+09
   0.064204 Path: UPS.ffff00ff.ffff00d7, Type: Feature, ReportID: 0xc3,
Offset: 0, Size: 32, Value: 2562
   0.064955 Path: UPS.ffff00ff.ffff00ef, Type: Input, ReportID: 0xe3,
Offset: 0, Size: 8, Value: 0
   0.065015 Path: UPS.ffff00ff.ffff00ef, Type: Feature, ReportID: 0xe3,
Offset: 0, Size: 8, Value: 0
   0.065089 Report descriptor retrieved (Reportlen = 885)
   0.065135 Found HID device
   0.065178 Detected a UPS: Tripp Lite/AVR900U
   0.065230 find_nut_info: unknown info type: load.off.delay
   0.065273 find_nut_info: unknown info type: load.on.delay
   0.065315 find_nut_info: unknown info type: load.off.delay
   0.065374 upsdrv_initinfo...
   0.065467 upsdrv_updateinfo...
   0.066954 Got 1 HID objects...
   0.067017 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 3650
   0.067065 Quick update...
   0.067229 dstate_init: sock /var/run/nut/usbhid-ups-tripplite open on fd 5
   0.067300 upsdrv_updateinfo...
   0.195017 Got 9 HID objects...
   0.195120 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.195194 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.195284 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.195361 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.195439 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   0.195494 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 1
   0.195545 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.195608 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.195657 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.195722 Quick update...
   2.068005 upsdrv_updateinfo...
   2.197223 Got 1 HID objects...
   2.197303 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 94
   2.197348 Quick update...
   4.071967 upsdrv_updateinfo...
   4.201458 Got 1 HID objects...
   4.201533 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 3649
   4.201574 Quick update...
   6.072388 upsdrv_updateinfo...
   6.201718 Got 9 HID objects...
   6.201804 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   6.201863 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   6.201917 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   6.201981 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   6.202036 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
   6.202088 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 1
   6.202139 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   6.202195 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   6.202249 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   6.202291 Quick update...
   8.074300 upsdrv_updateinfo...
   8.203949 Got 1 HID objects...
   8.204037 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 94
   8.204083 Quick update...
  10.076166 upsdrv_updateinfo...
  10.205204 Got 1 HID objects...
  10.205305 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 3650
  10.205355 Quick update...
  12.078075 upsdrv_updateinfo...
  12.207436 Got 9 HID objects...
  12.207952 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type:
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
  12.208103 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
  12.208249 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x32, Offset: 16, Size: 1, Value: 1
  12.208626 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x32, Offset: 18, Size: 1, Value: 0
  12.208775 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input,
ReportID: 0x32, Offset: 19, Size: 1, Value: 0
  12.209140 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x32, Offset: 20, Size: 1, Value: 1
  12.209289 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x32, Offset: 21, Size: 1, Value: 0
  12.209656 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type:
Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
  12.209798 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
  12.210143 Quick update...
  14.079987 upsdrv_updateinfo...
  14.209670 Got 1 HID objects...
  14.209753 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x34, Offset: 0, Size: 8, Value: 94
  14.209795 Quick update...
  16.081844 upsdrv_updateinfo...
  16.210923 Got 1 HID objects...
  16.211041 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x35, Offset: 0, Size: 16, Value: 3649
  16.211181 Quick update...


Should I run this without -x explore? Is there a way to get upsdrvctl to
send the option -x productid=3024 to usbhid-ups? Would that be a good idea?

 ~ Paul Nickerson
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to