Thanks for the reply. However these two FAQ are unfortunately not describing 
the situation. 
- The first issue is that NUT switches off the UPS upon reboot on low battery 
(not that it dies because of low battery)
- The second issue is that the UPS does not recognise being online again (not 
that the PC does not restart)

Sent from my iPhone

> On 11 Jun 2019, at 02:03, Charles Lepple <[email protected]> wrote:
> 
>> On Jun 10, 2019, at 2:32 PM, Marc Finns wrote:
>> 
>> Hello, I read all FAQ and other sources but I could not find this situation, 
>> so I thought of asking the experts.
>> I successfully configured a Raspberry NUT server to control my UPS that 
>> powers several devices (NUC with ESXI VMs, Synology NAS etc).
>> All works well in principle, but I have the following behaviours that I 
>> could not find described anywhere.
>>    • When power returns after the system has shuts down because of battery 
>> flat, all restarts immediately. However, as soon as NUT server reboots, it 
>> switches the UPS to battery till it dies – even if line is present
> 
> This is FAQ #49: 
> https://networkupstools.org/docs/FAQ.html#_my_ups_powers_up_immediately_after_a_power_failure_instead_of_waiting_for_the_batteries_to_recharge
> 
>>    • If power returns after the system has started the shutdown sequence, 
>> the UPS does not return to AC mode and stays on battery till it dies.
> 
> This is FAQ #51:
> 
> https://networkupstools.org/docs/FAQ.html#_the_power_came_back_during_the_shutdown_but_before_the_ups_power_off_now_the_ups_does_not_reboot_and_my_computer_stays_off_how_can_i_fix_that
> 
> These are subtle edge cases, but apparently a lot of entry-level UPS models 
> omit the interface to control these two situations. As mentioned in both of 
> the FAQ explanations, you can work around this in software, or you can sell 
> the UPS to someone who annoys you, and look for one that provides the 
> "battery.charge.restart" NUT variable (Minimum battery level for UPS restart 
> after power-off) and the "shutdown.return" instant command.
> 
> In both cases, we have tried to collect NUT variable dumps and command 
> listings from NUT users here: https://networkupstools.org/ddl/
> 
> Note that this information is best-effort, and sometimes vendors change the 
> underlying firmware without changing the model name. There is no substitute 
> for testing when it comes to shutdown procedures, unfortunately. 
> 
> (If you get an error from the mailing list about the message size, please try 
> turning off HTML posting, and gzip any log files.)
> 
>> 
>> Therefore, behaviour (1) creates a dangerous endless loop where power 
>> returns, all boots, after 30 sec power is brutally cut, and so on. The net 
>> result is that I already killed a disk.
>> Please note: I never had this behaviour when I used the Synology as network 
>> UPS server.
>> Is anyone having the same / having a suggestion?
>> Thanks a million. Marc.
>> 
>> Hardware: Raspberry PI
>> OS name and version: Raspbian (Linux raspberrypi 4.19.42-v7+ #1219 SMP Tue 
>> May 14 21:20:58 BST 2019 armv7l GNU/Linux)
>> NUT version 2.7.4 installed from repo
>> UPS: APS Back-UPS RS 550G 
>> Driver configuration:
>> [ups]
>>        driver = usbhid-ups
>>        port = auto
>>        desc = "Back-UPS RS 550G"
>>       ignorelb
>>       override.battery.charge.low = 20
>>       override.battery.runtime.low = 200
>>       pollfreq = 15
>> 
>> Output of  /lib/nut/usbhid-ups -DD -a ups
>> Network UPS Tools - Generic HID driver 0.41 (2.7.4)
>> USB communication driver 0.33
>>   0.000000   debug level is '2'
>>   0.004536   upsdrv_initups...
>>   0.006506   Checking device (051D/0002) (001/004)
>>   0.009744   - VendorID: 051d
>>   0.009826   - ProductID: 0002
>>   0.010240   - Manufacturer: American Power Conversion
>>   0.010866   - Product: Back-UPS RS 550G FW:857.L5 .I USB FW:L5  
>>   0.011214   - Serial Number: 3B1547X04970  
>>   0.011271   - Bus: 001
>>   0.011768   - Device release number: 0090
>>   0.011822   Trying to match device
>>   0.012248   Device matches
>>   0.013822   HID descriptor length 1134
>>   0.016761   Report Descriptor size = 1134
>>   0.019750   Using subdriver: APC HID 0.96
>>   0.019824   112 HID objects found
>>   0.020801   Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, 
>> Offset: 0, Size: 8, Value: 2
>>   0.021529   Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 
>> 0x02, Offset: 0, Size: 8, Value: 3
>>   0.022404   Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
>> ReportID: 0x03, Offset: 0, Size: 8, Value: 4
>>   0.023913   Path: UPS.PowerSummary.iOEMInformation, Type: Feature, 
>> ReportID: 0x04, Offset: 0, Size: 8, Value: 1
>>   0.025154   Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 
>> 0x05, Offset: 0, Size: 8, Value: 1
>>   0.026405   Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, 
>> Offset: 0, Size: 8, Value: 1
>>   0.027244   Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, 
>> Offset: 0, Size: 8, Value: 1
>>   0.028082   Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: 
>> 0x06, Offset: 8, Size: 8, Value: 0
>>   0.028965   Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 
>> 0x06, Offset: 8, Size: 8, Value: 0
>>   0.029785   Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: 
>> 0x06, Offset: 16, Size: 8, Value: 8
>>   0.030618   Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 
>> 0x06, Offset: 16, Size: 8, Value: 8
>>   0.031914   Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, 
>> ReportID: 0x07, Offset: 0, Size: 16, Value: 18290
>>   0.033288   Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 
>> 0x08, Offset: 0, Size: 16, Value: 12
>>   0.034536   Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x09, 
>> Offset: 0, Size: 16, Value: 12.59
>>   0.035776   Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 
>> 0x0a, Offset: 0, Size: 8, Value: 1
>>   0.037025   Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 
>> 0x0b, Offset: 0, Size: 8, Value: 2
>>   0.038282   Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
>> ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>>   0.039169   Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
>> ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>>   0.040008   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 
>> 0x0c, Offset: 8, Size: 16, Value: 262
>>   0.040842   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 
>> 0x0c, Offset: 8, Size: 16, Value: 262
>>   0.042150   Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 
>> 0x0d, Offset: 0, Size: 8, Value: 100
>>   0.043790   Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, 
>> ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
>>   0.045030   Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, 
>> ReportID: 0x0f, Offset: 0, Size: 8, Value: 50
>>   0.046289   Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, 
>> ReportID: 0x10, Offset: 0, Size: 8, Value: 1
>>   0.047658   Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, 
>> ReportID: 0x11, Offset: 0, Size: 8, Value: 10
>>   0.048905   Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, 
>> ReportID: 0x12, Offset: 0, Size: 8, Value: 1
>>   0.050153   Path: UPS.PowerSummary.ACPresent, Type: Input, ReportID: 0x13, 
>> Offset: 0, Size: 8, Value: 1
>>   0.050693   Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 
>> 0x13, Offset: 0, Size: 8, Value: 1
>>   0.051529   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: 
>> Input, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>>   0.051760   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: 
>> Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>>   0.052150   Path: UPS.PowerSummary.ShutdownImminent, Type: Input, ReportID: 
>> 0x14, Offset: 8, Size: 8, Value: 0
>>   0.052536   Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, 
>> ReportID: 0x14, Offset: 8, Size: 8, Value: 0
>>   0.053409   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, 
>> ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>>   0.054039   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
>> ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>>   0.054279   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, 
>> ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>>   0.054497   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, 
>> ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>>   0.054959   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
>> Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>>   0.055360   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
>> ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>>   0.055752   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
>> ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>>   0.056148   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
>> Input, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>>   0.056541   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
>> Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>>   0.056957   Path: 
>> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
>> ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>>   0.057713   Path: 
>> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
>> ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>>   0.059206   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
>> Input, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>>   0.059435   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
>> Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>>   0.059909   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, 
>> Type: Input, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>>   0.060331   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, 
>> Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>>   0.060733   Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: 
>> Input, ReportID: 0x16, Offset: 7, Size: 1, Value: 0
>>   0.060957   Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: 
>> Feature, ReportID: 0x16, Offset: 7, Size: 1, Value: 0
>>   0.061353   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
>> Input, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>>   0.061752   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
>> Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>>   0.062147   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
>> ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>>   0.062550   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, 
>> ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>>   0.063188   Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: 
>> Input, ReportID: 0x16, Offset: 10, Size: 1, Value: 0
>>   0.063408   Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: 
>> Feature, ReportID: 0x16, Offset: 10, Size: 1, Value: 0
>>   0.064299   Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, 
>> ReportID: 0x17, Offset: 0, Size: 16, Value: 120
>>   0.065154   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.065791   Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 
>> 0x1c, Offset: 0, Size: 24, Value: 599297
>>   0.066410   Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 
>> 0x20, Offset: 0, Size: 16, Value: 19752
>>   0.067027   Path: UPS.Battery.Test, Type: Input, ReportID: 0x21, Offset: 0, 
>> Size: 8, Value: 6
>>   0.067247   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 
>> 0, Size: 8, Value: 6
>>   0.067906   Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID: 
>> 0x22, Offset: 0, Size: 8, Value: 18
>>   0.068533   Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 
>> 0x23, Offset: 0, Size: 16, Value: 262
>>   0.069157   Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID: 
>> 0x24, Offset: 0, Size: 16, Value: 120
>>   0.069783   Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, 
>> Offset: 0, Size: 16, Value: 12
>>   0.070424   Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, 
>> Offset: 0, Size: 16, Value: 12.59
>>   0.071043   Path: UPS.Battery.ff860024, Type: Feature, ReportID: 0x27, 
>> Offset: 0, Size: 16, Value: 247
>>   0.071667   Path: UPS.Battery.ff860018, Type: Feature, ReportID: 0x28, 
>> Offset: 0, Size: 32, Value: -1.34135e+09
>>   0.072280   Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, 
>> Offset: 0, Size: 8, Value: 230
>>   0.072912   Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 
>> 0, Size: 16, Value: 235
>>   0.073536   Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 
>> 0x32, Offset: 0, Size: 16, Value: 176
>>   0.074160   Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 
>> 0x33, Offset: 0, Size: 16, Value: 282
>>   0.074783   Path: UPS.Input.ff860024, Type: Feature, ReportID: 0x34, 
>> Offset: 0, Size: 16, Value: 128
>>   0.075399   Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, 
>> Offset: 0, Size: 8, Value: 1
>>   0.076023   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 
>> 0x36, Offset: 0, Size: 8, Value: 0
>>   0.076649   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: 
>> Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>>   0.077279   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: 
>> Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>>   0.077902   Path: UPS.APCGeneralCollection.DelayBeforeShutdown, Type: 
>> Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: -1
>>   0.078529   Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 
>> 0x50, Offset: 0, Size: 8, Value: 26
>>   0.079478   Path: UPS.PowerConverter.ff860024, Type: Feature, ReportID: 
>> 0x51, Offset: 0, Size: 8, Value: 226
>>   0.080454   Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, 
>> ReportID: 0x52, Offset: 0, Size: 16, Value: 330
>>   0.081163   Path: UPS.ff860001.ff860023, Type: Feature, ReportID: 0x60, 
>> Offset: 0, Size: 16, Value: 0
>>   0.081788   Path: UPS.ff860001.ff860026, Type: Feature, ReportID: 0x61, 
>> Offset: 0, Size: 8, Value: 138
>>   0.082900   Path: UPS.ff860001.ff860025, Type: Feature, ReportID: 0x62, 
>> Offset: 0, Size: 32, Value: 5.0463e+07
>>   0.083531   Path: UPS.iProduct, Type: Feature, ReportID: 0x7f, Offset: 0, 
>> Size: 8, Value: 5
>>   0.084150   Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, ReportID: 
>> 0x7e, Offset: 0, Size: 8, Value: 7
>>   0.084774   Path: UPS.iSerialNumber, Type: Feature, ReportID: 0x7d, Offset: 
>> 0, Size: 8, Value: 3
>>   0.085397   Path: UPS.iManufacturer, Type: Feature, ReportID: 0x7c, Offset: 
>> 0, Size: 8, Value: 1
>>   0.086029   Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, 
>> Offset: 0, Size: 16, Value: 18290
>>   0.086659   Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 
>> 0x7a, Offset: 0, Size: 1, Value: 1
>>   0.086916   Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: 
>> 0x7a, Offset: 1, Size: 1, Value: 0
>>   0.087155   Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 
>> 0x7a, Offset: 2, Size: 1, Value: 1
>>   0.087368   Path: UPS.PresentStatus.BatteryPresent, Type: Feature, 
>> ReportID: 0x7a, Offset: 3, Size: 1, Value: 1
>>   0.087585   Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: 
>> Feature, ReportID: 0x7a, Offset: 4, Size: 1, Value: 0
>>   0.087804   Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, 
>> ReportID: 0x7a, Offset: 5, Size: 1, Value: 0
>>   0.088017   Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: 
>> Feature, ReportID: 0x7a, Offset: 6, Size: 1, Value: 0
>>   0.088231   Path: UPS.PresentStatus.CommunicationLost, Type: Feature, 
>> ReportID: 0x7a, Offset: 7, Size: 1, Value: 0
>>   0.088447   Path: UPS.PresentStatus.NeedReplacement, Type: Feature, 
>> ReportID: 0x7a, Offset: 8, Size: 1, Value: 0
>>   0.088668   Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 
>> 0x7a, Offset: 9, Size: 1, Value: 0
>>   0.088887   Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, 
>> ReportID: 0x7a, Offset: 10, Size: 1, Value: 0
>>   0.089537   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 
>> 0, Size: 8, Value: 0
>>   0.090152   Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x78, 
>> Offset: 0, Size: 8, Value: 1
>>   0.090785   Path: UPS.ff860029, Type: Feature, ReportID: 0x75, Offset: 0, 
>> Size: 16, Value: 98
>>   0.092051   Path: UPS.ff86002a, Type: Feature, ReportID: 0x74, Offset: 0, 
>> Size: 32, Value: 3.0318e+08
>>   0.092948   Path: UPS.ff860090.ff860091, Type: Feature, ReportID: 0x8c, 
>> Offset: 0, Size: 8, Value: 1
>>   0.093576   Path: UPS.ff860090.ff860092, Type: Feature, ReportID: 0x8d, 
>> Offset: 0, Size: 8, Value: 25
>>   0.094305   Path: UPS.ff860090.ff860093, Type: Feature, ReportID: 0x8e, 
>> Offset: 0, Size: 8, Value: 36
>>   0.094758   Path: UPS.ff860090.ff860094, Type: Feature, ReportID: 0x8f, 
>> Offset: 0, Size: 8, Value: 0
>>   0.095293   Path: UPS.ff860090.ff860095, Type: Feature, ReportID: 0x90, 
>> Offset: 0, Size: 8, Value: 1
>>   0.095763   Path: UPS.ff860090.ff860096, Type: Feature, ReportID: 0x91, 
>> Offset: 0, Size: 16, Value: 4
>>   0.096259   Path: UPS.ff860090.ff860097, Type: Feature, ReportID: 0x92, 
>> Offset: 0, Size: 16, Value: 4
>>   0.096757   Path: UPS.00000000.ff000055, Type: Feature, ReportID: 0x80, 
>> Offset: 0, Size: 8, Value: 0
>>   0.096884   Report descriptor retrieved (Reportlen = 1134)
>>   0.096919   Found HID device
>>   0.096954   Detected a UPS: American Power Conversion/Back-UPS RS 550G 
>> FW:857.L5 .I USB FW:L5  
>>   0.097057   Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
>> ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>>   0.097169   Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, 
>> ReportID: 0x0f, Offset: 0, Size: 8, Value: 50
>>   0.097273   Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 
>> 0x23, Offset: 0, Size: 16, Value: 262
>>   0.097423   Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, 
>> Offset: 0, Size: 16, Value: 12.59
>>   0.097553   Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, 
>> Offset: 0, Size: 16, Value: 12
>>   0.097676   Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
>> ReportID: 0x03, Offset: 0, Size: 8, Value: 4
>>   0.098542   Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 
>> 0x20, Offset: 0, Size: 16, Value: 19752
>>   0.098659   Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 
>> 0x1c, Offset: 0, Size: 24, Value: 599297
>>   0.098762   Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 
>> 0x50, Offset: 0, Size: 8, Value: 26
>>   0.098951   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, 
>> ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>>   0.099201   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: 
>> Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>>   0.099280   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 
>> 0, Size: 8, Value: 6
>>   0.099361   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.099448   Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, 
>> Offset: 0, Size: 16, Value: 18290
>>   0.099551   Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, 
>> ReportID: 0x52, Offset: 0, Size: 16, Value: 330
>>   0.099663   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
>> ReportID: 0x16, Offset: 2, Size: 1, Value: 1
>>   0.099740   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
>> Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0
>>   0.099817   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, 
>> ReportID: 0x16, Offset: 0, Size: 1, Value: 1
>>   0.099889   Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
>> Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0
>>   0.099964   Path: 
>> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
>> ReportID: 0x16, Offset: 4, Size: 1, Value: 0
>>   0.100036   Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, 
>> ReportID: 0x16, Offset: 9, Size: 1, Value: 0
>>   0.100118   Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
>> Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0
>>   0.100193   Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, 
>> Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0
>>   0.100274   Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
>> Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1
>>   0.100346   Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, 
>> Offset: 0, Size: 8, Value: 1
>>   0.100415   Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 
>> 0x06, Offset: 8, Size: 8, Value: 0
>>   0.100485   Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 
>> 0x13, Offset: 0, Size: 8, Value: 1
>>   0.100555   Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: 
>> Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0
>>   0.100621   Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, 
>> ReportID: 0x14, Offset: 8, Size: 8, Value: 0
>>   0.100685   Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 
>> 0x06, Offset: 16, Size: 8, Value: 8
>>   0.100754   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 
>> 0x36, Offset: 0, Size: 8, Value: 0
>>   0.100829   Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 
>> 0x36, Offset: 0, Size: 8, Value: 0
>>   0.100898   Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 
>> 0, Size: 16, Value: 235
>>   0.100980   Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, 
>> Offset: 0, Size: 8, Value: 230
>>   0.101103   Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 
>> 0x32, Offset: 0, Size: 16, Value: 176
>>   0.101197   Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 
>> 0x33, Offset: 0, Size: 16, Value: 282
>>   0.101277   Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, 
>> Offset: 0, Size: 8, Value: 1
>>   0.101492   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 
>> 0, Size: 8, Value: 6
>>   0.101581   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 
>> 0, Size: 8, Value: 6
>>   0.101668   Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 
>> 0, Size: 8, Value: 6
>>   0.101735   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 
>> 0, Size: 8, Value: 0
>>   0.101803   Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 
>> 0, Size: 8, Value: 0
>>   0.101914   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, 
>> ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>>   0.102004   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, 
>> ReportID: 0x15, Offset: 0, Size: 16, Value: -1
>>   0.102169   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: 
>> Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>>   0.102249   Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: 
>> Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1
>>   0.102311   Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: 
>> Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0
>>   0.102403   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.102478   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.102556   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.102625   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.102696   Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
>> ReportID: 0x18, Offset: 0, Size: 8, Value: 1
>>   0.102831   find_nut_info: unknown info type: load.on.delay
>>   0.102880   find_nut_info: unknown info type: load.on.delay
>>   0.102946   upsdrv_initinfo...
>>   0.102995   upsdrv_updateinfo...
>>   0.103404   Got 2 HID objects...
>>   0.103475   Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
>> ReportID: 0x0c, Offset: 0, Size: 8, Value: 18
>>   0.103552   Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 
>> 0x0c, Offset: 8, Size: 16, Value: 262
>>   0.103596   Quick update...
> 

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to